Sparky Required! ha! Home Mains Powered smoke alarms

StrawDog

Forum Supporter
I think this is wired up correctly. Had to use the old wiring so spliced some of the old wrap and I think I should be good to go.. ?

ROOM A (mains feed from ECB)

20200205_165059.jpg

ROOM B

20200205_164136.jpg
 

steptoe

TK Veteran
Forum Supporter
if you are fitting all new alarms then the following is generally regarded as "standard" ( not a definite rule though )
Brown - permanent live
Black - interlink ( trigger )
Grey - neutral

use AICO alarms, they are simply the best for the price point.
 

StrawDog

Forum Supporter
red and blue coming from the mains, old wiring there mate, and also old wiring between room, probably newer than the red/blue from ECU.
 

steptoe

TK Veteran
Forum Supporter
ye, your red & black (blue oversleeve) is your live and neutral in, the brown,black,grey between the alarms is post 2007 and should be used as live, trigger , neutral , in that order
 

StrawDog

Forum Supporter
so all looks good? just waiting on some cable and some connectors to hook it all together.
 

StrawDog

Forum Supporter
can't use smoke alarms mate, vaping set's them off...LOL, heat alarms better than nothing, yeah there has to be heat/fire but better than nowt... wiring all looks good then? cheers pal.
 

Smurfsworld

Registered
can't use smoke alarms mate, vaping set's them off...LOL, heat alarms better than nothing, yeah there has to be heat/fire but better than nowt... wiring all looks good then? cheers pal.
The aico optical should not be set off by vape according to them
 